hi I am new to the forum and new to the electrical trade , Just completed my 2330 level 3 , got my 17th Edition , am in the process of trying to gain some experience , I have an opportunity to do some work for a friend who is a plumber,
The jobs needed to be done are down lighters and underfloor heating in 2 bathrooms and some light switch circuits and sockets moving , I am confident I can move the lighting circuits and the sockets , but I am not getting involved with the down lighters and the underfloor heating , the house is on 3 storeys and the electrics are supplied via a old type fuse board , My concerns are that the lighting circuit in the bathroom should be RCD protected and the underfloor heating should be on a separate circuit and also RCD protected , are my concerns valid , any advice would be a great help . I don't want to refuse the job completely because there are more opportunities on the horizon ,
 
if you are modifying circuits that enter the bathroom then they need rcd protection. just quote for the job including adding a new consumer unit. don't be turning jobs down just because you need to add an rcd.
 
If you are not getting involved with the downlights and the underfloor heating then I would not worry too much about them.

However all low voltage circuits in or through a bathroom must be protected by a 30mA RCD.
Underfloor heating can be on a socket circuit but consideration should be given to overloading a point on a ring.
If the underfloor heating is greater than 2 kW then a separate circuit would be a good idea.
 
If you are not getting involved with the downlights and the underfloor heating then I would not worry too much about them.

However all low voltage circuits in or through a bathroom must be protected by a 30mA RCD.
Underfloor heating can be on a socket circuit but consideration should be given to overloading a point on a ring.
If the underfloor heating is greater than 2 kW then a separate circuit would be a good idea.
If the OP isn't the question is who is? Paul the plumber, Barry the bathroom fitter.
 
if you're moving stuff around and not removing it then the cable if buried is going to require protecting by rcd or earthed metal conduit or surface mounting. if you're putting new sockets in then they need rcd protection.
 

Reply to concerns working in bathroom in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I
  • Article
Water underfloor heating and epoxy grouts Hello, I did some reading here and there, but the opinions seem to diverge at some point and I am not...
Replies
0
Views
111
istefanov87
I
Bit of a sickener they didn't employ you to do the box change aint it? I might, as a disclaimer, point out with that certificate that as the...
Replies
2
Views
564

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top