W
willy1984
Hi there,
I'm planning a shed supply project in order to get my part p...
The concrete shed is going to have 3 double sockets and 4 strip lights. There is a spare way in the house CU.
The shed is roughly 50 metres along from the house CU.
Here is my plan...
From the spare way in the CU, 6mm SWA cable fixed to the garden fence (or underground) on a 40A RCBO supplying a garage consumer unit with 30mA RCD. From here, a 1mm cabled radial lighting circuit on 6A breaker and a ring circuit for the sockets using 2.5/1.5mm cable on a 30A breaker...
Does this sound any good?!?!
Willy:D
if PME sorry TN-C-S supply then you have to provide seperate earth for garage ie rod and RCD
re yesterdays post
have contacted NIC tech help and verdict is to use rod and RCD at garage end
this is to prevent the extension of the equipotential zone and any problems bonding now or in future
and is to comply with the esqc regs which i wiil check and post back findings
re yesterdays post
The NIC need to read GN8 and probably the Regs while they're at it.
They also need to realise that they don't make the rules.:)
They are annoying when they come up with their own regulations that are in contradiction with BS7671:mad:
Reply to Concrete shed supply... in the Australia area at ElectriciansForums.net
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Haha yes, it is. Must be a northern expression. Have a Google 😂
Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...