Hi guys,

As a way of learning/getting my head around the regs I do mock condition reports if I see something I don't think is quite right but some of these things I wouldn't know what to code (If anything) If anyone can give me their thoughts it'd be much appreciated!

- At a friends house:RCD Protected. 2x 10mm main bond, one is connected to the gas, the other would be for the water but we couldn't find the connection. The incoming water is metal and not plastic but the kitchen uses a mixture of copper and plastic fittings. I'd probably code this a C2.
- A door frame has been notched to fit over a switch so the switch is not accessible. I'd code C3 reg 134.1.1 and 132.12
- RCD protected circuit, at a surface mounted plastic switch there is no earth terminal and the earth is loose. I don't think this would warrant a code but would the screws be an exposed conductive part and therefore need earthing?
- A light fitting is mounted only with 1 screw instead of 3 so is hanging loose. I think I'd code this a C3 as it's connected to the fixed wiring. Reg 134.1.1

Thanks for any advice or input, reading the regs for fun isn't that fun sometimes.
 
A hanging loose light fitting would in most cases, be a code C2 for me.

Just found this.

559.5.2 Fixing of luminaires

'Adequate means to fix luminaires shall be provided'
'The fixing mans may be mechanical accessories, boxes or enclosures which are able to support luminaires or supporting devices for connecting a luminaire.'
 
The 10mm to the water i would test the continuity of it to the MET as if the reading is less than 0.05 ohm i would just code it a C3 as cant find bonding clamp if not (within reason) then would C2 it.

The door frame i would also code a C3.

The switch where the earth is not connected but is present i would code this a C3 if it was just a free conductor in the back of the swotch but if it is in a connector block or something like that then I would not code it.

The light fitting not having all the screws put in as long as the fittig is secure and not flapping about i would not code it but if its loose and could fall off i would code it a C2.
 
Just out of
The 10mm to the water i would test the continuity of it to the MET as if the reading is less than 0.05 ohm i would just code it a C3 as cant find bonding clamp if not (within reason) then would C2 it.

The door frame i would also code a C3.

The switch where the earth is not connected but is present i would code this a C3 if it was just a free conductor in the back of the swotch but if it is in a connector block or something like that then I would not code it.

The light fitting not having all the screws put in as long as the fittig is secure and not flapping about i would not code it but if its loose and could fall off i would code it a C2.
just out of interest if you performed a continuity test to determine whether bonding was in place and the reading was acceptable why still a code 3? Could you not state that furthur investigstion was required?
 
If continuity is proven then I would code further investigation to locate the bonding connection for the water. It could well be hidden by Kev the kitchen fitter and could cause quite a lot of damage trying to locate it.
 

Reply to Condition report practice in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
621
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
504

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top