But that is your first step?But there is my conundrum, just a few feet of wire will limit the fault current significantly.
But there is my conundrum, just a few feet of wire will limit the fault current significantly.
Ok, say I have a 2.5mm2 or 3.31mm2 copper conductor 90*C rated. 100,000 amps of available fault current. 277/480 volt Y system, TN-C-S. MCB protection. Would the conductor survive such a short circuit? How do I determine this?
But that is your first step?
- Determine Zs at the end point (supply Ze and the cable resistances R1+R2) to get the PFC
- From the PFC and OCPD determine disconnect time
- From the conductor CAS, conductor material, and insulation temperature limits compute the I2t limit from the adiabatic equation
- Compare the resulting PFC^2 * time with the I2t limit for your conductor
how exactly have you measured 100,000 amps of fault current ? Do you mean 10ka ?
Thing is you can get a short inches from the MCB/MCCB if someone failed to fit a grommet and the cable is cut by a metal enclosure's edge!Right, however how much should I assume at the start of the run? Few feet? More, less? The thing is the NEC doesn't give any guidance, and BS7671 seems to ask using fault current levels that are not likely to be encountered in reality ie I can't see a wire shorting to the enclosure 2 inches off the MCB.