I was at a job on Friday in a big 4 storey house. One of the jobs I was there to do was to add sockets to a bedroom which actually didn't have any at all. The top floor sockets were on there own breaker, a 32A RCBO actually. There were two 4mm^2 T&Es at the RCBO so I initially thought it was a ring. When I found the other ends of these cables in the top floor loft area, they were both terminated in a junction box and a 2.5mm^2 ring was run from there. So, a lollipop circuit with conductors in parallel forming the initial feed (the 'stick' of the lollipop). I actually didn't have time to start the sockets so I will be there tomorrow to do it.

I am interested to know who would leave the circuit as it is and just add the sockets to the ring part of the circuit, and who would convert the circuit into a full ring (easily done with an extra JB next to the existing one). The last option would obviously result in a ring with 4mm^2 legs of equal length and the 'loop' section in 2.5mm^2. Thanks!
 
Did you do a Zs on the existing set up?

If the Zs is low, could you disconnect on 4mm and redo it, to see if the Zs is OK

and then if it is then you could use the 4mm which is now spare and extend it to form a radial or another lollipop
 
maybe the 4mm was used to avoid volt drop? if i read yur OP right, you have a rfc with the initial feeders fun in 4mm. reducing to 2.5mm on the top floor.
 
I haven't done any tests yet, it was 4.30pm on Friday and I didn't want to start anything I had no chance of finishing. I think one 4mm would be adequate, the run can't be more than about 10 meters.

Tel - it's not a RFC, the feeders are joined in a JB and the ring is taken from there.
 
Since it is easy to get to the junction box then I would try and separate them into a ring. But with just three sockets is it worth the effort.
I have left a few lollipop rings in that situation where it is not possible to easily get to the point of junction, so long as it meets the regulations' requirements then it is just another circuit, albeit non standard. No, not a circuit that is not listed in the OSG, surely that is illegal!
 
Weird :)
I'd convert it to be an RFC - reason being to easily confirm ring continuity from board or any accessory (for some future test say). IIUC to convert it you just redo that jb?
 
I can easily convert it to a full ring by chopping a couple of sockets in nearby and taking the feeds into them then onto the existing and new sections of the ring. I could also create two radials at 20A, which may be a better option. Hmmm. The mind boggles.
 
Since it is easy to get to the junction box then I would try and separate them into a ring. But with just three sockets is it worth the effort.
I have left a few lollipop rings in that situation where it is not possible to easily get to the point of junction, so long as it meets the regulations' requirements then it is just another circuit, albeit non standard. No, not a circuit that is not listed in the OSG, surely that is illegal!

I do believe the circuit is fully compliant (pending the outcome of my tests tomorrow) as it is, and though not a 'standard circuit', it is a bit weird and in this case, pointless.

Do you have space for another RCBO?

Yes, it's a Wylex NSB type. Plenty of unused ways.
 

Reply to Conductors in parallel...... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
388
  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top