cliffed
Worcester
Helping out a fellow spark, 2nd fixing,nice school extension.
Have the regs changed,concerning cpc sizes with cables.
It’s all been specificed by consultant,the circuits are radials,which is a good thing.
Bit confused about the sizing of the cpc,obviously single cabling,4.0mm live & neutral,the strange thing is that the cpc is 2.5mm.
I always thought this should be 4.0mm,it this situation.
If your using galv why are you running a separate CPC?
Designers can't depend on the integrity of the installation nowadays and hence rightly specify separate CPC conductors.
The quality of kit available now is atrocious, brass bushes are paper thin and I'm comming across malleable boxes that are not threaded straight which is irksome for besa mounted lighting runs that you want perfectly lined up. I think most of this carp is now cast in China.
100% Agee with you regarding the crooked besa boxes, very disappointing
I was always taught,cpc same size in single cabling,conventionally/conservatively,this was always done.
Obviously using the abriactic equation,the cpc is smaller.
T/e is calculated for that purpose,most swa cabling the cpc are the same as the live & neutral.
Will be happy to do this now,after sizes were specified,on this job.
If I personal install cabling,most probably stick to cpc same size as live.
Other than that,the equation may be activated,& see how that performs.
Thanks for all replies.
In SWA the cpc is always a different size, and a different material for that matter. It’s only if you use a cable with an extra core (eg 3 core for single phase) to use as a cpc that you get one the same size.
I am not sure why you question it if you are helping a mate and someone else has design responsibility.
I know that they come up with some stupid calculations, but they have to put their name to the certification.
That said I do enjoy the 20m 4.0mm2 rings
Reply to Conduit cabling sizes in the UK Electrical Forum area at ElectriciansForums.net
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...