Hi guys after advice

Large old manor hall wiring 30 yrs old. Tn-c-s Few faults rectified and board changed to 17th edition.

Downstairs orginally had a ring wired in steel conduit and singles. Using the conduit as a earth. Look like a door way was put on to make a extension to the house a few years ago and in doibg so a socket was removed and jb put in its place. The conduit has been bent down to below ground level and it is at this point where the ring is no longer a ring.

I split the ring on to 2xb20

Leg 1 = 0.58 r1+r2 0.83 zs
Leg 2 = 45.6 r1+r2 45.8 zs

The final socket on leg 2 actually gets 0.61 and 0.86 but every other socket back to the board is in the 45 ohm range.

The house is registered with english heritage and the owner is looking to sell. Lot of expense rewiring.Tried running new earth in the conduit but to no avail.

The garage is fed from a fuse spur on this radial. I was thinking bout dropping a rod external to the garage and on the the db board in the garage. This should lower my zs on all but one of the sockets. ( assuming I am correct with my evaluation of where a break in the conduit seems to be)

Am I right in thinking there is nothing wrong with dropping a rod as suggested or anyone any other suggestions.
 
I'd make more enquires as to who left it in that condition and I'd hunt them down, then drag them back to re-instate the conduit to complete the ring (earth connection is paramount), then explain to the owner of the building what a dangerous state it had been left in.
 
The conduit has been bent down to below ground level and it is at this point where the ring is no longer a ring.

I split the ring on to 2xb20

Am I right in thinking there is nothing wrong with dropping a rod as suggested or anyone any other suggestions.

So, is the conduit itself in the form of a ring (ie two ends connected to the DB), or is it just the circuit that was wired as a ring?

Why did you split the ring?

Using earth rods to make up for a break in CPC sounds like a bodge to me.
 
You wouldn't improve the Zs one bit with a rod. What you'd effectively be doing is making the circuit TT.
theoretically, you'll already be covered for the high Zs as its on an RCD (or should be)
how do you know it's high impedance on the CPC? Have you got end to end readings, and R1 + Rn readings?
This is a difficult one to remedy properly due to English heritage. They won't want surface mounted trunking/conduit.
 
High zs values are accepted on a tt system with both 30mA and 100ma in the hope that in the event of a failure of one rcd a .4 disconnection time can still be achieved.

Putting a 100ma rcd time delayed before the board at source is a option. I dont believe dropping a rod at source and changing to a tt is making the system safer even thou the system would then comply.
 
I know its tn c s and as it stands it doesnt comply. But add 100ma rcd and make it tt and and it does.

My argument is adding the 100ma rcd makes sense with valid reasoning but removing the supplied earth and providing a higher ze for the rest of the circuits by putting in a rod is making the installation more unsafe then just adding 100ma rcd and keeping the lower provided earth path

I hope you can understand my thinking
 
Yeah I understand you're thought but even with adding rods and making it a TT there's still a break in the cpc of this RFC and no amount of adding the magic RCD will fix that.
 

Reply to conduit ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
712

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top