Hi guys after advice
Large old manor hall wiring 30 yrs old. Tn-c-s Few faults rectified and board changed to 17th edition.
Downstairs orginally had a ring wired in steel conduit and singles. Using the conduit as a earth. Look like a door way was put on to make a extension to the house a few years ago and in doibg so a socket was removed and jb put in its place. The conduit has been bent down to below ground level and it is at this point where the ring is no longer a ring.
I split the ring on to 2xb20
Leg 1 = 0.58 r1+r2 0.83 zs
Leg 2 = 45.6 r1+r2 45.8 zs
The final socket on leg 2 actually gets 0.61 and 0.86 but every other socket back to the board is in the 45 ohm range.
The house is registered with english heritage and the owner is looking to sell. Lot of expense rewiring.Tried running new earth in the conduit but to no avail.
The garage is fed from a fuse spur on this radial. I was thinking bout dropping a rod external to the garage and on the the db board in the garage. This should lower my zs on all but one of the sockets. ( assuming I am correct with my evaluation of where a break in the conduit seems to be)
Am I right in thinking there is nothing wrong with dropping a rod as suggested or anyone any other suggestions.
Large old manor hall wiring 30 yrs old. Tn-c-s Few faults rectified and board changed to 17th edition.
Downstairs orginally had a ring wired in steel conduit and singles. Using the conduit as a earth. Look like a door way was put on to make a extension to the house a few years ago and in doibg so a socket was removed and jb put in its place. The conduit has been bent down to below ground level and it is at this point where the ring is no longer a ring.
I split the ring on to 2xb20
Leg 1 = 0.58 r1+r2 0.83 zs
Leg 2 = 45.6 r1+r2 45.8 zs
The final socket on leg 2 actually gets 0.61 and 0.86 but every other socket back to the board is in the 45 ohm range.
The house is registered with english heritage and the owner is looking to sell. Lot of expense rewiring.Tried running new earth in the conduit but to no avail.
The garage is fed from a fuse spur on this radial. I was thinking bout dropping a rod external to the garage and on the the db board in the garage. This should lower my zs on all but one of the sockets. ( assuming I am correct with my evaluation of where a break in the conduit seems to be)
Am I right in thinking there is nothing wrong with dropping a rod as suggested or anyone any other suggestions.