Conduit runs over 10 meters

2

2396help

Hi, as my name says im just trying to do the project on my 2396, im looking into my options of cable management and on route i have stumbled across conduit rating factors p142 yellow osg (ive never worked with conduit) and the rating factors only go up to 10m, is this 10m maximum length or 10m maximum length between inspection boxes

Many thanks
 
Welcome to the forum, may I tempt you into applying for our trainee section where you are amongst like minded trainee's and we have mentors to help with the kind of questions asked by those learnng the ropes, it's not a requirement but I would recommend it :)
 
Hi bud,is it plastic or steel conduit? because other factors will be at play,not least,earthing and thermal expansion :stooge_curly:
 
In days of old we fitted a pull in box every two lengths of conduit, or every two 90º bends or two double sets.
 