Icn = n for knackered, means it is capable of breaking this magnitude of fault current and is the absolute max capacity but will not work again after, this is the parameter for the EICR, for clearing the largest fault current that is possible (or pfc).
Nope it's Icn, same as for the MCB/RCBO (normally 6k or 3k for the wylex plug in 3036 replacement jobbies).Isnt it the other way round ?
I thought the value recorded on the cert was its Ics ? the max fault current that leaves the mcb reusable ?
Its certainly the most useful data of the two.
For breakers to BS EN 60898 the Icn and Ics are the same up to and including 6kA
Reply to Conflicting informatiom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net