I have a TT earthing system with a 63Amp (30ma)RCD Garage unit.
my ze reading earth disconnected is 169 ohms - happy with that falls within range.
when i do a 3 lead test on my fluke for pfc gives me 1 A reading - also happy with this
ohms reading with 3 test lead is 194
when i do zs i get a reading of 195ohms, my R1+R2 Reading is 0.4, it seems that my ze reading should be more inline with the 3 lead pfc test reading.
Am i missing something here, any experienced help would be appreciated.
PAUL
I have a TT earthing system with a 63Amp (30ma)RCD Garage unit.
my ze reading earth disconnected is 169 ohms - happy with that falls within range.
when i do a 3 lead test on my fluke for pfc gives me 1 A reading - also happy with this
ohms reading with 3 test lead is 194
when i do zs i get a reading of 195ohms, my R1+R2 Reading is 0.4, it seems that my ze reading should be more inline with the 3 lead pfc test reading.
Am i missing something here, any experienced help would be appreciated.