Confused readings testing TT Ze with fluke 1653 | on ElectriciansForums

Discuss Confused readings testing TT Ze with fluke 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Paul Willoughby

Afternoon

I have a TT earthing system with a 63Amp (30ma)RCD Garage unit.

my ze reading earth disconnected is 169 ohms - happy with that falls within range.

when i do a 3 lead test on my fluke for pfc gives me 1 A reading - also happy with this
ohms reading with 3 test lead is 194

when i do zs i get a reading of 195ohms, my R1+R2 Reading is 0.4, it seems that my ze reading should be more inline with the 3 lead pfc test reading.

Am i missing something here, any experienced help would be appreciated.

PAUL
 
Last edited by a moderator:
well, i would not be happy with 169ohms. that would give a pefc of 1.36A. the bonding to the water/gas must be giving you this 1kA. get a decent rod installed before eng54 comes on and slaps your legs.
 
Now, what's the betting that the DNO earthing system has been left at the house??


As for being happy with either of those values, ...dear oh dear!!
 
Last edited by a moderator:
Have dropped another rod in and now have Ze of 115ohms and PFC of 2.1 A

Is it worth me changing the RCD or should I just calculate ZS, the RCD passes RCD test ok.
 
Have dropped another rod in and now have Ze of 115ohms and PFC of 2.1 A

Is it worth me changing the RCD or should I just calculate ZS, the RCD passes RCD test ok.

I wouldn't be too happy with that value either ..lol!! Oh and it's NOT Ze, it's Ra when talking about a TT systems earth electrode!!

Do you have a DNO supplied TN-S/TNC-S earthing point at the house, or is the house on a TT system as well??
 
so now you have discovered that the 3 ft long twiggies are useless as earth rods. go out and buy 5/8" screw together rods. 2 or 3 of these getting depth of 7ft. to 11 ft. might just give you a decent Ra/Ze.
 
At least 2 or possibly 3 5/8th rods coupled together, they fit lovely inside a kango 900's chuck and can be hammered into pretty much any surface in seconds, i've just done a tt today, 3 rods coupled gave a healthy 2 ohms :) Perhaps i hit the water main :D
 
I wouldn't be too happy with that value either ..lol!! Oh and it's NOT Ze, it's Ra when talking about a TT systems earth electrode!!

Do you have a DNO supplied TN-S/TNC-S earthing point at the house, or is the house on a TT system as well??

DNO supplied TNCS at the house, swa run to garage TT as earthing for garage, Ze / Za on certificate is zs at db, I have joined to 4ft 5/8th rods together and still only get 115ohms, will this value not suffice? ground is very hard and dry, I have even tried running the hose on it.
 
so why on earth ( no pun intended) have you not used the TNC-S that is a better earth than any rod?
 
No extraneous parts in garage.

Reason for not exporting earth is: One of the potential faults with exporting an earth from a TN-C-S (PME) head end is that consideration needs to be given if the suppliers neutral were ever disconnected but the live left unaffected. This would leave the neutral and the earth floating. Given it would be connected to the live side of the supply via all your appliances, and there would be no current flowing, the potential of the neutral and earth (and by implication the metal cases of all your appliances) would tend to rise to 240V. This obviously raises a serious shock risk.

or have i got this all wrong, phoned Elecsa and they recommended using earth rods for anything over 10meters from the house and getting the lowest earth reading possible under recommended values.

Information overload here.
 
Paul,

surely the chance of that happening applies to about 40 million homes in the uk therefore they should all be TT'd or converted back to TNS....
 
No extraneous parts in garage.

Reason for not exporting earth is: One of the potential faults with exporting an earth from a TN-C-S (PME) head end is that consideration needs to be given if the suppliers neutral were ever disconnected but the live left unaffected. This would leave the neutral and the earth floating. Given it would be connected to the live side of the supply via all your appliances, and there would be no current flowing, the potential of the neutral and earth (and by implication the metal cases of all your appliances) would tend to rise to 240V. This obviously raises a serious shock risk.

or have i got this all wrong, phoned Elecsa and they recommended using earth rods for anything over 10meters from the house and getting the lowest earth reading possible under recommended values.

Information overload here.
If this was such a high risk they would make us earth rod as back up also, export the earth
 

Reply to Confused readings testing TT Ze with fluke 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
277
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top