solution. use the PME buyt leave the rods in just in case . sssimpleess.
 
use the TN-C-S then your Ze will be below 0.35 ohms or should be lol so the PFC will be a lot better and not jsut relying on a RCD to hopefullly work and disconnect in the required time

I used a 6mm 3 core swa to supply my bruvs shed a run of about 30 metres and all Zs comply so the RCD is only there for additonal protection this job was used for my assessment I wanted to use 10mm to lower Vd as it was close in the end with final circuits for the lights but within the 3% max and the 5% for power for the sockets and 4mm swa 3 core which then feeds a double socket and FCU on decking all comply with Zs, and Vd
I am with ELCSA and was given was awarded an A and congratulated on my design
 
Last edited:
Now, what's the betting that the DNO earthing system has been left at the house??

I just knew that he had left a perfectly good earth at the house and was struggling to get a decent Ra level with a rod!!

Forgive the Pun, but your just making a rod for your own back. Leave the rod in the ground and it's connection to your garage CU and use that PME earth connection at the garage CU. Forget all the scaremongery you've been told it's rubbish. There is nothing wrong with extending a PME earth out to a garage, where you will have a very respectful min Ze of 0.35 ohms or thereabouts, rather than a limp 115 ohm Ra!!
 
Took advice and used PME earth at garage with 3rd core and by SWA Gland to earthing terminal, zs at db reading of 0.45 ohms.

Just confirming this is acceptable as this reading would now be Ze of the TNCS supply + R1+R2 of the SWA.

Yes?
 
Last edited by a moderator:
Now Zdb at your sub-board, which is Ze (at origin) + (R1+R2) of your sub-main (armoured cable).

You only have one Ze, this is at the origin
 

Reply to Confused readings testing TT Ze with fluke 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
390
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top