installed a secondary 2 way consumer unit to run a boiler and immersion heater i know i have to issue an eic but what do i actually test? r1 + r2 of the radial to the secondary consumer unit and both radials from the secondary consumer? please can someone give me a rundown of what id need to test?
 
You will need to perform all the tests required to complete the fields on the EIC. Methods for performing these tests are described on your On-Site Guide.
If you have installed new circuits in a domestic property this is notifiable work under the Part P of the Building Regulations and you are required to notify the Local Authority Building Control.
I assume you are not able to self-certify the work so can expect to pay them for the privilege of inspecting it for you.
 
Have 2 schedules of test results one for the first CU showing your new circuit to the 2 way CU and the other schedule showing the new circuits on the CU that you installed. 1 inspection sheet and all the other details needed. All tests required apart from ring continuity if you have no ring finals
 
yes i know you have to contact building control you ever tried talking to newham building control? they dont even know what they are doing. ive got 2391 and 2392 but get told all different things some people saying you have to re test the whole board even the old circuits which i didnt think was right i just thought it was the new circuits your installing you had to test
 
t6h
Have 2 schedules of test results one for the first CU showing your new circuit to the 2 way CU and the other schedule showing the new circuits on the CU that you installed. 1 inspection sheet and all the other details needed. All tests required apart from ring continuity if you have no ring finals


thankyou andy
 
Your description of works on the EIC is what you need to do ..



So something like ..... Install new circuit number ?? And install 2nd fuseboard and new circuits for .....

You have to ensure earthing and bonding are up to spec, plus your circuits must comply with the latest regs.

On your schedule of results for the existing board, I would use state "used" for existing circuits, and spare for any unused.
 
The Certsure on-line certification, uses the phrase 'NOT WOKED ON' for those circuits, not worked on! Succinct and to the point.
 
installed a secondary 2 way consumer unit to run a boiler and immersion heater i know i have to issue an eic but what do i actually test? r1 + r2 of the radial to the secondary consumer unit and both radials from the secondary consumer? please can someone give me a rundown of what id need to test?
It's R1+R2, r1,r2and rn are end to end resistances.
 

Reply to confused with procedure need help in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
297
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
174

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top