Tony Way

-
Arms
Joined
Dec 15, 2009
Messages
92
Reaction score
42
Location
Cambridgshire
Speccing a re-wire in bungalow with separate garage (1m from house) and a new shed/workshop to be 5m from house.

Bungalow on TT rod - no option for TNS orTNCS conversion

Now back in my learning days, I am sure that I was told that any separate building must have its own earthig arrangement ie rod.

I have been told recently that it is fine to export the main bonding via SWA third core and/or sheeth to a separate building. Although not sure that is correct.

Also if I use a separate earth for each building, I should not RCD the distribution circuit as each shed/garage should have CU and RCDs - therefore no discrimination between RCDs in series. But if I don't RCD the distribution circuit only protection for SWA would be MCB. - Is this enough?

Confused of ********** would appreciate any assistance.

Many thanks
 
don't work in UK but the sub-main will need ADS via 'main rcd' and mcb(tt)

the additional 30ma protection shouldn't be needed for a swa submain-if i'm understanding the uk rules correctly
 
Last edited by a moderator:
Had the exact same situation on friday bungalow on a TT with a shed/out building.The NIC basically said no need to put another rod in for the shed you can utilise the houses rod. As for the submain It needs protecting with a 100mA time delay RCD. then you get discrimination between the submain protection and the garage boards 30mA RCD. The shed supply I put in was protected with a 30mA RCBO at the consumer unit in the house as the customer didn't want a garage 2 way unit to save money, It does the power and lighting. The NIC didn't really think it was worth trying to discriminate between the power and lighting as it wasn't an inhabitable room. Every circuit on a TT system has to have RCD protection.
 
Last edited by a moderator:
so is that the existing 100mA main rcd that protects the new sub-main? -obviously it must be

sorry i'm not very familiar with tt

(don't want to hijack the post-may help though)
 
Last edited by a moderator:
Any circuit on a TT must have RCD protection because of disconnection times.

Therefore there is no need for a rod in the garage or an RCD in the sub board.
 
i thought the 100 mA 'main rcd' was enough for the sub-main here and then additional 30ma's in shed

It would have to be time delayed or you would lose both the garge 30mA and the 100mA RCD in the consumer unit in the house. Far easier putting the submain on the 30mA side of the house consumer unit and use that as the protection for the garage then you don't need to spend out for RCD board in the garage It's just a bit of a nusainace if the garage starts tripping the RCD in the house CU.
 
Last edited by a moderator:
ya time delayed upstream-i get it anyway:D

i would have the garage separate-to avoid the nuisance
 
Last edited by a moderator:

Reply to Confusion over earthing arrangements for Garages and sheds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top