Hello,

The shed is supplied with 6mm Swa on a 25amp rcbo. Inside the shed is a 20amp socket circuit and a 5 amp lighting circuit.

Can I add a junction box to the supply cable about mid way and radial off that box to a double socket?

a 32amp radial requires 4mm, and a 20amp radial is 2.5mm. But is there anything saying I can’t add a double socket to a shed supply cable when the cable size and rcbo both seem satisfactory?

thank you for reading and helping if you can
 
Agreed, should be ok providing it’s done properly: ie
Glanded properly to the new socket making sure that the earthing if the armour is properly carried through the new socket to the shed. Do you know how to terminate SWA cable?

Sounds like the SWA is not buried then and that you have enough slack in the cable to insert the socket?
 
Hello,

The shed is supplied with 6mm Swa on a 25amp rcbo. Inside the shed is a 20amp socket circuit and a 5 amp lighting circuit.

Can I add a junction box to the supply cable about mid way and radial off that box to a double socket?

a 32amp radial requires 4mm, and a 20amp radial is 2.5mm. But is there anything saying I can’t add a double socket to a shed supply cable when the cable size and rcbo both seem satisfactory?

thank you for reading and helping if you can
No not a good idea
 
the existing SWA is in reality a distribution curcuit. , i'd prefer to run a 2.5mm SWA from shed sockets back to the new external socket.
Presently it's a distribution circuit with a 25a RCBO protective device, not ideal. Add a socket halfway along and it becomes a final circuit with a DB at the far end the only useful purpose of which is downrating the lighting OCPD. The DB could equally be replaced by one or two FCU's for the power and lighting. But whats the point, the DB achieves the same result.
Of course the OP could do as you suggest, indeed it would be preferable, but what he proposes is absolutely fine if it's more practical.
 
the existing SWA is in reality a distribution curcuit. , i'd prefer to run a 2.5mm SWA from shed sockets back to the new external socket.
The SWA has been installed as a DISTRIBUTION CIRCUIT, if you meed a socket halfway from the outbuilding wire it from the CU
 
The SWA has been installed as a DISTRIBUTION CIRCUIT, if you meed a socket halfway from the outbuilding wire it from the CU
or wait till that clever bloke dyson invents a wireless socket. it will not work, however once the 12 month guarantee has expired.
 
thanks for the replies everyone.

i can terminate swa fine. i'll use the wiska earth nuts to bond the armour.

wiring a second swa along the same route as the 6mm just for the sockets sounds like it would be ugly as it's going to be all surface mounted.

the internal shed sockets are 2.5mm radials off the shed cu's 20amp breaker.

I could put in a 20 amp rcbo instead of the 25, do away with the CU in the shed and just have the lights off a spur on the sockets so that it's just one long socket circuit?
 
.

I could put in a 20 amp rcbo instead of the 25, do away with the CU in the shed and just have the lights off a spur on the sockets so that it's just one long socket circuit?
That would be fine and probably the best option if your preferred method is to install the socket on the 6.0mm SWA.
Three options are now on the table. Your original proposal, the option of wiring from the shed DB which you have discounted, and the above you yourself have suggested. All three are viable and safe if correctly carried out.
 
the existing SWA is in reality a distribution curcuit. , i'd prefer to run a 2.5mm SWA from shed sockets back to the new external socket.
Sounds the best option.

Depending on the route, slack, etc, if you try cutting and joining mid-cable you run the risk of running out of free cable to do the job properly (if at all).
 

Reply to Connect Sockets To Shed Supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
  • Question
Tech has totally complicated 'control' Customer wants something controlling. First job is to figure out the best method
    • Funny
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top