Just wanted to check something with the great and the good on here, I'm just about to put in a aeg induction hob in my kitchen, the two diagrams show one 400v diagram with the two lives going to connection points 1 and 2, the 230v diagram (relevant to me) shows the live going to connection point 2 but with a bridge/loop also connected to connection point 1 from connection point 2 this makes sense but I wanted to check on here. For info I am using 6mm cable on its own 32amp mcb hob is 4.7 kW.
Thanks for any replies