Hi all, is it ok to connect the main incoming neutral to a 3 phase db directly to the neutral bar and avoiding the main isolator?
Thx
The db came with a 4 pole isolator but I've been told it's ok to connect it straight to the neutral bar?
Surely this is bad practice?
If you’ve got a 4 pole isolator then use it.
Generally tho in a TN system you can use a 3 pole isolator to isolate the phases only,as the neutral is considered to be around the same potential as earth as they are connected together at the transformer/supply end.
TT 3 phase supply then the neutral needs to be isolated also.
Generally there’s a neutral terminal on the main switch with 3 pole type on some manufacturers types were the neutral connects but isn’t switched.
Domestic single phase consumer units tho require double pole isolation as used by ordinary persons or unskilled electrically or whatever the hell it is nowadays.
Doesn't matter the means of supply for a TN system, submain or the origin. Neutral is deemed to be at earth potential on TN systems and there is no requirement to isolate it. This is not the case for TT and isolation is required.
why would you want to do this? surely it'd be easier to connect it to the isolator as the other 3 phases are going there too
Reply to Connecting the neutral directly to the neutral bar in the Commercial Electrical Advice area at ElectriciansForums.net
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.