Hi all, is it ok to connect the main incoming neutral to a 3 phase db directly to the neutral bar and avoiding the main isolator?
Thx
 
The db came with a 4 pole isolator but I've been told it's ok to connect it straight to the neutral bar?
Surely this is bad practice?
If you’ve got a 4 pole isolator then use it.
Generally tho in a TN system you can use a 3 pole isolator to isolate the phases only,as the neutral is considered to be around the same potential as earth as they are connected together at the transformer/supply end.
TT 3 phase supply then the neutral needs to be isolated also.
Generally there’s a neutral terminal on the main switch with 3 pole type on some manufacturers types were the neutral connects but isn’t switched.

Domestic single phase consumer units tho require double pole isolation as used by ordinary persons or unskilled electrically or whatever the hell it is nowadays.
 
Last edited:
Doesn't matter the means of supply for a TN system, submain or the origin. Neutral is deemed to be at earth potential on TN systems and there is no requirement to isolate it. This is not the case for TT and isolation is required.
 
why would you want to do this? surely it'd be easier to connect it to the isolator as the other 3 phases are going there too
 

Reply to Connecting the neutral directly to the neutral bar in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
643
All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.
Replies
13
Views
974

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top