Not unusual to want to monitor power of a motor, it provides better protection for the connected mechanical load than the motor overload. The mech load may well be damaged if jammed, by the time the motor overload has got around to tripping....essentially the power meter is acting as a shearpin.
You wont need separate CT's for such a small motor, the power monitor would be connected directly to the monitoring relays...have a look at uk.rs-online.com/web/p/monitoring-relays/0465258/ or similar. All this monitor would do is unlatch your starter circuit, not display the actual true power, although pricier ones do.
If you are wanting to display the motor current have a look at www.crompton-instruments.com/datasheets/Analogue_Instruments_REV_04-10.pdf some connected via CT's some directly connected.
A typical monitoring device only displays, what your talking about is a much more expensive protective device!! The OP has stated that it is only to check current and voltage, not very fine over current protection!!