Hi all
for a straight consumer change with out new circuits being added am i right in saying that you pir the installation then pirs are not notifiable hence no building controle !!!! only asked as thats what it seems says in gn3
thanks
Rich
 
Hey tucker.

For a c.u change you would need to use an EIC, not PIR.

ON the EIC you just fill in what you have done in the extent covered box, i.e upgrading of consumer unit and bonding etc. Then test all circuits as normal.

Cheers
 
What he said^^^, however, you should put right any major deviations ie lack of main bonding etc.

I always carry out a PIR prior to a CU change because you never know what nasties may be lurking that may catch you out.
 
What he said^^^, however, you should put right any major deviations ie lack of main bonding etc.

I always carry out a PIR prior to a CU change because you never know what nasties may be lurking that may catch you out.
surely this adds more cost to the customer , what i do is explain what problems could occur ie new 17th board could start tripping or no ring continuity and put in writing any of this extra work would have to be carried out on a ttime and materials basis then your covered when all the nasties pop .
 
Indeed, but, as i said, any major deviations need rectifying as well.

Have always explained this to the customer and never had one turned down yet.

Especially if the install looks like its been altered or is reasonably old.
 
Indeed, but, as i said, any major deviations need rectifying as well.

Have always explained this to the customer and never had one turned down yet.

Especially if the install looks like its been altered or is reasonably old.
its a good point id say both ways work just as well, as in my case estimate to install bonding and replace c.u, inform client you would then carry out a test on the whole of the installation and issue a report of its condition with an estimate for cost of repairs if any .
 

Reply to consumer exchange pir/eic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Yes that does appear to be the case. I may get an electrician to fit the correct glands. Thank you.
Replies
10
Views
451
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top