Hi all, I phoned my governing body yesteday to ask the dreaded question about TT system with metal consumer unit. His reply was that a tails gland should be used with clamp for tails in board and a 100mA rcd as main switch to protect tails feeding 30mA rcd's. He also said a fire resistant material should be used in plastic trunking above board to stop fire escaping past holes where cables enter the board and setting the trunking on fire. I said I thought as long as ip ratings for horizontal and vertical edges were met there wasn't a requirement for the board to be fire rated. His reply was that anywhere air could get in or fire could escape from should be sealed else there is no point fitting a metal board.
We both finally agreed that I could fit a 100mA rcd in plastic enlosure before board as it woudn't be classed as switch gear (wylex also recommed this practice on there youtube video even though I disagree and think it should be classed as switchgear).
I understand eveything he said, but where do you stop with extra expense for materias, labour etc
I just wondered how far the rest of you go and what practices you would recommend in this situation. Thanks in advance.