P

pencilpusher

I have three questions re changing a CCU: I have seen the "CCU change and you" thread but I don't believe it mentions anything about inspection dates.

1) I believe I need to put "Consumer Unit change only" on the periodic label but what date do I put for the next inspection. I am working towards 2391 but have done a periodic of sorts before changing the CU. However, I am not qualified to do periodics yet.

2) I have installed 2 Hager RCD's and 1 hager RCBO. The RCBO trips at 19mA and the RCD's at 21mA. I was expecting something between 25-29 mA. Are these trips currents normal for a 30mA RCD/RCBO.

3) On the schedule of inspections I can tick most boxes but not the "cables in safe zones" becuase I cannot be sure. I presume LIM goes in there?

Thanks PP
 
I have three questions re changing a CCU: I have seen the "CCU change and you" thread but I don't believe it mentions anything about inspection dates.

1) I believe I need to put "Consumer Unit change only" on the periodic label but what date do I put for the next inspection. I am working towards 2391 but have done a periodic of sorts before changing the CU. However, I am not qualified to do periodics yet.

If it's domestic, max 10 years or on change of owner, change of usage ... unless condidition or usage of the instalation dictates otherwise.

2) I have installed 2 Hager RCD's and 1 hager RCBO. The RCBO trips at 19mA and the RCD's at 21mA. I was expecting something between 25-29 mA. Are these trips currents normal for a 30mA RCD/RCBO.

A little on the low side, take them back to the wholesaler for exchange.

3) On the schedule of inspections I can tick most boxes but not the "cables in safe zones" becuase I cannot be sure. I presume LIM goes in there?

That should be N/A on the EIC.
LIM on a EICR/PIR, just make sure that it's also agreed with the owner.


Thanks PP

Inserts in blue.
 
Last edited:
Thank you topquark. My point is that I don't have 2391 so am not doing periodics as such but with the tests I have done for this CU change, I have done these tests anyway to ensure all is OK. If I put 10 years then I am saying I have done a periodic when I shouldn't do really. The tests done help me to know that this installation is safe before CU change. Am I making sense here?

Thanks PP
 
Thank you topquark. My point is that I don't have 2391 so am not doing periodics as such but with the tests I have done for this CU change, I have done these tests anyway to ensure all is OK. If I put 10 years then I am saying I have done a periodic when I shouldn't do really. The tests done help me to know that this installation is safe before CU change. Am I making sense here?

Thanks PP
Ten years would be the default for a new installation (or complete rewire), hence being the max you would state. Only you can determine, based on your testing results, what's appropriate for the next inspection. You will have to guage that by how old the existing instalation is, it's condition and the usage (I assume it's domestic). It's not really a question anyone (who hasn't seen the instllation) can answer for you.
 
Thank you topquark. My point is that I don't have 2391 so am not doing periodics as such but with the tests I have done for this CU change, I have done these tests anyway to ensure all is OK. If I put 10 years then I am saying I have done a periodic when I shouldn't do really. The tests done help me to know that this installation is safe before CU change. Am I making sense here?

Thanks PP
No reason why you can't conduct a PIR, or state when you consider the next inspection should be.
There is no requirement for an Inspector to have a qualification.
 
your RCD trip times may be lower than expected if you are testing with loads /circuits connected. this is because there may be a small amount of leakage on the installation.
 
I have three questions re changing a CCU: I have seen the "CCU change and you" thread but I don't believe it mentions anything about inspection dates.

1) I believe I need to put "Consumer Unit change only" on the periodic label but what date do I put for the next inspection. I am working towards 2391 but have done a periodic of sorts before changing the CU. However, I am not qualified to do periodics yet.

2) I have installed 2 Hager RCD's and 1 hager RCBO. The RCBO trips at 19mA and the RCD's at 21mA. I was expecting something between 25-29 mA. Are these trips currents normal for a 30mA RCD/RCBO.

3) On the schedule of inspections I can tick most boxes but not the "cables in safe zones" becuase I cannot be sure. I presume LIM goes in there?

Thanks PP


You will need to issue an Electrical Installation Certificate for the consumer unit change regardless of whether you carried out a PIR or not.

On the schedule of inspections, you should enter N/A for items such as 'safe zones' as the schedule will only relate to the work that you have carried out.
 
You will need to issue an Electrical Installation Certificate for the consumer unit change regardless of whether you carried out a PIR or not.

On the schedule of inspections, you should enter N/A for items such as 'safe zones' as the schedule will only relate to the work that you have carried out.

Yep OK. There will be a lot of N/A's I suspect for a CCU change then?
 

Reply to Consumer unit change and RCD ramp testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
303
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top