pencilpusher
I have three questions re changing a CCU: I have seen the "CCU change and you" thread but I don't believe it mentions anything about inspection dates.
1) I believe I need to put "Consumer Unit change only" on the periodic label but what date do I put for the next inspection. I am working towards 2391 but have done a periodic of sorts before changing the CU. However, I am not qualified to do periodics yet.
2) I have installed 2 Hager RCD's and 1 hager RCBO. The RCBO trips at 19mA and the RCD's at 21mA. I was expecting something between 25-29 mA. Are these trips currents normal for a 30mA RCD/RCBO.
3) On the schedule of inspections I can tick most boxes but not the "cables in safe zones" becuase I cannot be sure. I presume LIM goes in there?
Thanks PP