S

SB-LEC

Been asked to change a consumer unit

On inspection found out that customer had done much of the work himself - approx 20 years ago

Currently has old Wylex NN Board

Ring Mains & Kitchen appear OK - T&E

Lights have no cpc, except for a couple with metal fittings.

The lights with metal fittings have an earth, but is borrowed from the ring main.

Q1, Am I OK to change CU with warning notices attached

Q2, What action is required about the borrowed CPC

Q3, AM I OK to run sepearte CPC to fittings without going via switches.

SB-LEC
 
If the customer wont pay for a rewire or running a separate 4mm cpc (Just as cheap to rewire in twin and earth) then you can change the consumer unit, Providing of course main bonding is up to scratch.Making sure IR global is more then 2.0m or individually 1.0m

Id be changing all class 1 fittings and replacing them with class 2.. Borrowing cpc is bad crack as a fault on the sockets will be transfered onto the lights.
 
No. Advice to the client is replace class 1 fittings with classs II and put a note on the EIC and the appropropriate label on the CU.

Check with your scheme, but this is the advice Elecsa hand out.
 
Murdoch

Have read the Best practice guide and everything points towards me suggeting a lighting re-wire
]

If they agree then go for it.. If they don't then follow the advice in the event they wont pay for a rewire..

Most importantly explain the options and most importantly the costs.. They can make the decision based on that.. But you cant insist on a partial rewire in order to change the consumer unit..
 
No. Advice to the client is replace class 1 fittings with classs II and put a note on the EIC and the appropropriate label on the CU.

Check with your scheme, but this is the advice Elecsa hand out.

I second that..

OP.. Whats your main bonding like? If ever in doubt phone your scheme (Presuming of course your registered)

May as well get your moneys worth for your annual fee
 
Class ll change should be OK, but customer does not want to change metal clad fittings.

There is a spare 6mm CPC running from the CU to the attic space for some reason.

I'm assuming i can utilise this for the metal fitting and take appropriate action as per best parctice guide

SB-LEC
 
Class ll change should be OK, but customer does not want to change metal clad fittings.

There is a spare 6mm CPC running from the CU to the attic space for some reason.

I'm assuming i can utilise this for the metal fitting and take appropriate action as per best parctice guide

SB-LEC

In which case you should make doubly sure that the customer is aware of the class I issues. That said their house is far safer with RCD protection on the other sockets so its much safer than before...... or you could walk away and leave it non RCD and class I!!
 
Last edited by a moderator:
Class ll change should be OK, but customer does not want to change metal clad fittings.

There is a spare 6mm CPC running from the CU to the attic space for some reason.

I'm assuming i can utilise this for the metal fitting and take appropriate action as per best parctice guide

SB-LEC

the switches will also have to have cpc installed in order to fit class 1 fittings. If you using the 6mm to connect then make sure every thing is connected to the same and connected via the light fitting to the switch.

Having the cpc to the fittings from one source and the switches connected to sockets IMO is bad crack..

With the age of the cable what are your IR values.. This would be the deciding factor next for me..
 

Reply to Consumer Unit Change - No CPC on lights - Borrowed earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
756
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top