Consumer Unit Change - No CPC on lights - Borrowed earth | Page 2 | on ElectriciansForums
Discuss Consumer Unit Change - No CPC on lights - Borrowed earth in the UK Electrical Forum area at ElectriciansForums.net
SB-LEC
Been asked to change a consumer unit
On inspection found out that customer had done much of the work himself - approx 20 years ago
Currently has old Wylex NN Board
Ring Mains & Kitchen appear OK - T&E
Lights have no cpc, except for a couple with metal fittings.
The lights with metal fittings have an earth, but is borrowed from the ring main.
Q1, Am I OK to change CU with warning notices attached
Q2, What action is required about the borrowed CPC
Q3, AM I OK to run sepearte CPC to fittings without going via switches.
SB-LEC
The ESC best practice guide on changing a CU when lighting circuits have no cpc says that a risk assessment should be carried out and, if the risk is low then the CU can be changed if the risk is High then it shouldn't
Reply to Consumer Unit Change - No CPC on lights - Borrowed earth in the UK Electrical Forum area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...