I suggest you check guide 6 here:
Best practice guides : Electrical Safety Council
especially the flow chart inside the back page.


So you leave a BS3036 board in place rather than install a dual RCD board because there's no bonding?? Don't get me wrong but I'd argue that the dual RCD board is much safer than the 3036 board, and we're supposed to be making sites safer.
 
I quite agree with all your views and know that in the best practice world, the one or two times a year this happens, I should throw my hands up in the air and walk away but do believe that only two things will happen from this, the customer will go to an unregistered sparky who will do the job for cash and not care whether or not anything is earthed, not just the water and gas and I'll have more problems paying the bills that month. I believe the client is better off having a full explanation on why it is needed and a new fuse board with the correct certificates showing any defects and recomendations than no paperwork at all. When I was talking specifically about this last year with ELECSA, they agreed. If this puts me in the firing line if something goes wrong then so be it but it will be the client at fault as I'll have their signature saying they wont carry it out to back me up. 'something' is much less likely to go wrong with a dual RCD board on an installation that's been tested than an old Wylex with no tets. I'm up for assesment next month and will bring it up again along with the two NICEIC sparkys in my area that I've caught changing consumer units because they need a spare way for a shower, only testing the new circuit and still not installing bonding. If the customer wanted a new shower circuit and didn't have bonding then yes, I'd walk. (I already know that ELECSA can't do anything about the dodgy NIC sparks, neither will the LABC, or even the NICEIC until the said sparky has been asked by the client to return and do it properly)
 
I have had a similar situation to Tonkatoy cant find any everdance of bonding to water or gas so what I did was did a continuity between the earth pin of the socket (CPC) and the copper water pipe and gas pipe.
Disconnected the earth (isolated supply of course) and I had a nice reading of less than 1ohm - didn't see any reason to start running 10mm anywhere just to satisfy 17th regs.
What ever was there has been fine for 50+ years and is still giving a nice continuity now!

At the end of the day you cant apply 17th regs for old installs (not under 17th regs).

I could not understand where on earth these pipes where getting an earth from but they where. No 10 mm in CU (that I could see) but saying that there was a 10mm connected to the supply pipes.
Customer didn't want me running 10mm around the house either.
I even did an RCD test (1x test) on the water as the earth and the RCD kicked in no problems at all so again not a clue!

(Yes I did reconnect the main earth before anyone asks!)
 
So you leave a BS3036 board in place rather than install a dual RCD board because there's no bonding?? Don't get me wrong but I'd argue that the dual RCD board is much safer than the 3036 board, and we're supposed to be making sites safer.


I hear what you are saying Murdoch, but the 3036 board has not got my name on it.

Iam with Nicholas here, No Bonding = No Work.
As Welchyboy pointed out you are leaving yourself wide open, and no letter is going to cover your arse, the customer is not a skilled person and therefore cannot make that choice (legally), you are the competent person onsite and the buck stops with you.
 
So you leave a BS3036 board in place rather than install a dual RCD board because there's no bonding?? Don't get me wrong but I'd argue that the dual RCD board is much safer than the 3036 board, and we're supposed to be making sites safer.

I have before - dont get me wrong the RCD wont work if a fault occurred and the pipes came live!
At the end of the day you signed that cert saying it complys with 17th regs (unless you state otherwise) If you install the CU and no bonding in place and someone is killed then good luck to anyone who thinks they can persuade the wigs that you acted in the best interests and inline with 17th regs and ESAWR (Electrical Safety at Work Regs) and HASWA 1974, etc

Everyone knows my opinion about RCDs, but I have once before walked out of a rental property (BS3036) inplace no bonding and informed LA Public Protection - within 1 hour they where around there and 1 hour later the landlord called me back to do it correctly!

To be honest I would rather do it that way and watch my back (and the family in the house) than please a landlord who clearly does not care about the safety of their tenants!
 
So you leave a BS3036 board in place rather than install a dual RCD board because there's no bonding?? Don't get me wrong but I'd argue that the dual RCD board is much safer than the 3036 board, and we're supposed to be making sites safer.


Not saying I've done it BUT what stops the weekend DIYer and the pub electrician - nothing!
 
One thing Public Protection told me

We have the same rights as Gas Safe Engineers

We cant disconnect a supply without permission (nor can they) - but we do (so do they)
The customer can turn it back on
The Gas Safe Engineer reports problems to LA Public Protection (SO SHOULD WE!)

The same law applies with rental properties - DUTY OF CARE - The landlord must supply a well maintained and safe electrical and gas supply!

Just because we are electricians , it does not mean we dont have a duty of care to the occupier of the property! - WE DO - SAME AS THE GAS SAFE ENGINEER

If your scared of bringing dangerous situations to the attention of someone who can reinforce the law and make them change it or lose the supply then you should rethink are you right to be an electrician with the responsibility of the public safety (WHICH WE ALL HAVE)
 
Not saying I've done it BUT what stops the weekend DIYer and the pub electrician - nothing!

The difference here is that there is no paper trail leading straight back to me!, what others do is no concern of mine, I only care about what I have done, and I know I can sleep easily at night having done the right thing.
 
One thing Public Protection told me

We have the same rights as Gas Safe Engineers

We cant disconnect a supply without permission (nor can they) - but we do (so do they)
The customer can turn it back on
The Gas Safe Engineer reports problems to LA Public Protection (SO SHOULD WE!)

The same law applies with rental properties - DUTY OF CARE - The landlord must supply a well maintained and safe electrical and gas supply!

Just because we are electricians , it does not mean we dont have a duty of care to the occupier of the property! - WE DO - SAME AS THE GAS SAFE ENGINEER

If your scared of bringing dangerous situations to the attention of someone who can reinforce the law and make them change it or lose the supply then you should rethink are you right to be an electrician with the responsibility of the public safety (WHICH WE ALL HAVE)

Public Protection?

What or who are you refering to?

Perhaps it might be a good idea to start a new thread and illucidate some more?
Who are these people?

what are their responsibilities?
what powers do they have?
what sort of things should be reported to them?
 
132.16 No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.

As I said, No Bonding = No work
 
Public Protection Officers or Environmental Health Officers/Practitioners (ENOs/ENPs) are responsible for enforcing the law within their county!
They have the right to issue improvement notices which must followed. If the person who was issued with these the EHP will issue them with a court summons where the Crown Court will issue them with an order to improve the situation or face jail.
 
132.16 No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.

As I said, No Bonding = No work


There you go - so clear and people still dont follow it!

Good luck to those who want to explain their action to the wigs!
 

Reply to Consumer Unit Changes - What make & what price? in the Business Related area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

Similar threads

Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
8K
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top