Consumer Unit Feed | Page 2 | on ElectriciansForums

Discuss Consumer Unit Feed in the UK Electrical Forum area at ElectriciansForums.net

Dunc88

-
Joined
Mar 22, 2017
Messages
29
Reaction score
4
Location
West Midlands
I've got an awkward job approaching where the consumer unit is to be relocated due to a semi-detached house being knocked into one. It's currently fed via a kmf & 16mm t&e, with a seperate 16mm earth. When the consumer unit is relocated, this wont be long enough, and even if it was this would have to be replaced with swa, to avoid requiring 30ma protection, and as it is >3M in length from the meter.
My questions are;
1. What size swa (will be 15+ circuits but no electric showers/cooker)
2. How many cores? 2core with seperate earth (& earth swa), or 3 core (& earth swa).
I'm thinking 3core 25mm, but surely not!?
Any help, advice appreciated!
Cheers!
 
OK,so the building work does not require removal of the one,remaining supply,so presumably,intake,metering etc,can stay in original location,with new DB situated in a new spot.

We don't know the nature of your supply/earth arrangements,but suggestions above seem suitable.

On the scale of costs,of the whole job,20m of 3C SWA,will be inconsequential.
Yes, thats right! Consumer unit couldnt go by the meter unfortunately as it backs onto the lounge & customer (despite my efforts) wont have it there! Thanks for your help peg
 
Yes, thats right! Consumer unit couldnt go by the meter unfortunately as it backs onto the lounge & customer (despite my efforts) wont have it there! Thanks for your help peg
But they don't mind a switch fuse being there because to terminate a three core, 25.0 swa into it it will be bigger than a matchbox.
 

Reply to Consumer Unit Feed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Issue is certain sizes of cable may theoretically be okay but upon the proper testing when it’s commissioned things like a thing may not test out...
Replies
8
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top