robd

-
Arms
Joined
Oct 21, 2010
Messages
688
Reaction score
398
Location
East Anglia
Morning all,

Just wired the 1st house on a new site, consumer unit wired to location marked on plan which was in kitchen unit at high level.

Building inspector comes in and okays everything but the consumer unit height, says they have to be at 1350-1450mm, was a new one on me and we ended up pulling in a few new legs in to allow for dropping it down abit. Funnily enough 1400 would've been half in and half out of the kitchen unit so it couldn't go at his stated height anyway.

Just wondered if anyone has a better knowledge of the building regs than me and could enlighten me, I know I asked the NIC in the past (for what it's worth) and they said no requirements other than accessible.

Cheers
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.
?

put it level with the top of the door like every other new build.

in my eyes its not functional, the circuits should not be switched back on till fault has been found and fixed.

there is no max hight for spotlights or batterns?

surely you swap the lamps more often than touch th ccu in your own home.


many people now have lived in there house for 5-10 years and dont know where the ccu is because they havent needed to use iit
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.

Where is this copied from?
 
the ccu can be at whatever height you want. personally as long as someone 6' can easily reach it.

put it above a door if you like and its still accessible

[ElectriciansForums.net] Consumer unit heights and building regs


[ElectriciansForums.net] Consumer unit heights and building regs
 
Comes down to the way you ask the question imo.
"I've not heard that one before mate, where does it come from?" is more likely to be well received than
"That's complete and utter BS you bloody clown. You haven't got a clue so show me where you get that from and I'll believe you"
Ah, calling em clock suckers was clearly impolite :D
 
I'm not a fan of putting them too low so kids can play with them. Also a mate of mine had his badly damaged in his new house with furniture removal men. While carrying his sofa into his house his CU was smashed and badly damaged! It needed replacing and I ended up having to sort it for him. Bloody mates rates!!
 
I'm not a fan of putting them too low so kids can play with them. Also a mate of mine had his badly damaged in his new house with furniture removal men. While carrying his sofa into his house his CU was smashed and badly damaged! It needed replacing and I ended up having to sort it for him. Luckily the removal mens insurance covered the cost of it.

i think you made a typo in your reply.
 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting


 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting


go for a bs88 board so there are no switches so they cant fail it lol
 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting



sitting on what? a stepladder?
 
Anyone ever had a successful arguement with building control that Part M only applies to new builds that are to be unoccupied on completion? (e.g. you dont know who is going to purchase the property so you have to assume it could be by say a wheelchair user and hence follow the Part M dimension guidlines. )

If doing an installation for a current owner then you re-wire to his spec for socket/switch heights, location of consumer unit etc ..... and Part M doesnt apply?

Not got the answer and never debated it before so be interesting to hear any views from anyone who has had the debate with an inspector .......
 

Reply to Consumer unit heights and building regs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top