Consumer unit in bathroom | on ElectriciansForums

Discuss Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 12, 2022
Messages
1
Reaction score
0
Location
Aylesbury
What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.

Thanks
 

Attachments

  • [ElectriciansForums.net] Consumer unit in bathroom
    E6E1F921-7BF1-46CC-8EF8-676393E1A395.jpeg
    365.9 KB · Views: 147
  • [ElectriciansForums.net] Consumer unit in bathroom
    D3438627-ADB4-4EFC-A218-CBE36CAB552F.jpeg
    350.3 KB · Views: 129
  • [ElectriciansForums.net] Consumer unit in bathroom
    BBD32DD6-A7A7-48A1-A029-BF03C65E7A2B.jpeg
    405.6 KB · Views: 129
consumer unit in zone 1
I am sure it is not going to be supported by the manufacturers instructions!!
 
It's a terrible design, but is it actually in zone 1 if it's in a cupboard?

Regulation prohibits socket outlets within 3 metres horizontally of the boundary of zone 1. ' The fact that it's in a cupboard doesn't stop it being used within the zone.
 
Last edited:
It's a terrible design, but is it actually in zone 1 if it's in a cupboard?
been pondering on that.
it is in zone 1 when the room is being used as expected, I.e. cupboard opened to get shampoo out whilst stood in bath.
with the door closed, you could argue that it is outside the zone.

Where do we go from here, is it acceptable to have a shaver socket in a shower cubical? NO

what if the shower head was removed could I say its not a shower, its a draught limiting enclosure for me to shave in?
 
That would help, however where in the regs dose it define a tool or a key as being a way of avoiding zones?

Generally speaking the zones stop at fixed partitions, walls etc. that do not move, and at the entrance door to the bathroom
 
It might just about meet regs on technicalities/or differing interpretations, but just because the regs don't specifically ban something doesn't mean we can't decide something is potentially dangerous.

I'd have no qualms deciding that I didn't like the environmental influences - steam and moisture. Also, as already said, the cupboard is easily left open, or easily opened while using shower, and shower spray becomes a huge concern.

The OSG mutters about an airing cupboard in a bathroom not being in zones. But that is a complete wall and door.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
The zone clearly extends to under the cupboard and there is nothing that effectively limits the zone, so for me it's in zone 1.
 
It might just about meet regs on technicalities/or differing interpretations, but just because the regs don't specifically ban something doesn't mean we can't decide something is potentially dangerous.

I'd have no qualms deciding that I didn't like the environmental influences - steam and moisture. Also, as already said, the cupboard is easily left open, or easily opened while using shower, and shower spray becomes a huge concern.

The OSG mutters about an airing cupboard in a bathroom not being in zones. But that is a complete wall and door.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
The zone clearly extends to under the cupboard and there is nothing that effectively limits the zone, so for me it's in zone 1.

I agree that there is nothing in the regs to say you can't do it, it's the socket outlet that bothers me as It's likely to be used otherwise there's no point in it being there.
 
I agree that there is nothing in the regs to say you can't do it, it's the socket outlet that bothers me as It's likely to be used otherwise there's no point in it being there.
No, I disagree with the comment "there is nothing in the regs to say you can't do it"
there are a few things that it may well fall foul of.
e.g.
in zone 1
a minimum rating of IP45 is required but it is generally accepted that IP65 is to be used.

can you be sure that the cupboard/db combination meets this??
 
No, I disagree with the comment "there is nothing in the regs to say you can't do it"
there are a few things that it may well fall foul of.
e.g.
in zone 1
a minimum rating of IP45 is required but it is generally accepted that IP65 is to be used.

can you be sure that the cupboard/db combination meets this??


IP rating for what ? Is it in Zone 1
 
YES IT IS IN ZONE 1

I see a cupboard in zone 1 containing electrical equipment.
what is the ip rating of the cupboard?

Ok how about a whirlpool bath that has a FCU /pump etc under the bath ? Is that IP rated ? no.

But it's ok because the bath has a side panel.

I'm not saying I agree with the situation, not at all.
 
It also needs to be fit for purpose. So ipx2 minimum for the environment.
An FCU isn't ipx2 and that's in zone 1 ? Under the bath.



Bear in mind, I don't agree with the Cu or socket outlet, but I am trying to find a definitive regulation that says no.

Look at #6
Regulation prohibits socket outlets within 3 metres horizontally of the boundary of zone 1. ' The fact that it's in a cupboard doesn't stop it being used within the zone.
 
In some older houses you have the airing cupboard in the bathroom with all the immersion switches and pumps and sometimes the heating JBs all slung in there etc

Being in a cupboard arguably takes it out of the zone in the same way a FCU being under a bath does, and in the same way an airing cupboard/partition door does.
 
I was asked to fit a socket under the bath for a shower pump last week, I agreed to put a RCD spur in the hall with a flex from it and wiska box under the bath. It would have been unnecessary risk to have it under there.
 
Being in a cupboard arguably takes it out of the zone in the same way a FCU being under a bath does, and in the same way an airing cupboard/partition door does.
The only problem I see with the cupboard door argument is say the home owner is in the bath/shower the lights trip , they lean over and reach to the consumer unit and get a 240v belt while resetting the breaker Would a the cupboad door argument hold up in court
 
I was asked to fit a socket under the bath for a shower pump last week, I agreed to put a RCD spur in the hall with a flex from it and wiska box under the bath. It would have been unnecessary risk to have it under there.
If it wasn't acceptable, we probably wouldn't have whirlpool baths.
 

Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

At some point, all sewage pumps will fail, or need extensive maintenance. I make it quite clear that I'm not interested in either.
Replies
16
Views
901
  • Question
There is also the ongoing problems if this is a gendered changing room.... For example, 2 or 3 burly male soldiers (you said it was an officers...
Replies
5
Views
664
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646
  • Question
ok cheers for the help lads
Replies
7
Views
576
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks