Hi All..thoughts on this please, is it acceptable or failed 'as not installed to manufactures instructions'?

Thanks in advance
20200313_141716 (1).jpg
 
Last edited by a moderator:
they're all the same lying down. Oops, that was meant to go in the preferences column of the eharmony dating site. :p :p :p
 
Agree that the MCBs are OK this way as they are in a 3-phase DB, but I think having the main switch in any orientation other than down=off is unacceptable as it could hinder isolation in an emergency. I believe the BS defines this but cannot offer a specific reference at the mo. Consider a fire crew working in the dark / smoke...

However DBs with a horizontally acting mainswitch do exist, the small (5 way iirc) 250A Merlin Gerin panelboards have the incoming device connected in the same orientation as the outgoing devices.
Also the old doorman death panelboards have the same arrangement.
 
I believe there is an issue here - essentially BS EN 61439 has that the main switch should operate on - in an upward direction, and it does not in this case, so even if the manufacturer doesn't specifically state anything it ought to be implied.

However I would check with the manufacturer themselves, Hager specifically state that they must be installed in the horizontal plane only, and from memory I have seen it with others as well.

If the manufacturer has stated a direction then it would warrant a C3 to me, if not I don't think there is sufficient justification to argue the point even though it is implied.

Now moving forwards with amd 1 and the 18th I think there are further issues - the principle of the compliant enclosures (BS EN 61439-3) is not just the material (the really, really ought to be metal thing), but that the enclosure should prevent movement of flame forward outwith the enclosure, which implies that the door should also ensure self-closure to enable this.

Now it isn't directly in BS EN 61439-3, but BEAMA have stated in their technical bulletin that the standard describes effective control of flame by having a case, a cover and a door in place.

... And that if the door may be left open, then in effect it isn't compliant.

Obviously this installation predates this, but is the case for anything since 2016

(and of course this metal and so on restriction only applies to homes, not commercial etc)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
dtec dave,
Last reply from
Julie.,
Replies
35
Views
10,319

Advert

TrueNAS JBOD Storage Server

Back
Top