Consumer unit MCB selection | on ElectriciansForums

Discuss Consumer unit MCB selection in the UK Electrical Forum area at ElectriciansForums.net

Spud1975

DIY
Joined
Oct 8, 2020
Messages
3
Reaction score
1
Location
Oxforx
Hi , looking for some advise please . So we had new house house rewired a year ago and had foresight to ask sparky to add MCB for garage with wire terminated in enclosure on outside of house in anticipation of extending it to detached garage at a later date once the internal renovation was completed. A year later and come to light that the spark has put in a 2.5mm cable on a 16a MCB. Feel this is a bit light would have preferred a 4mm cable and larger MCB , spark not to blame as I did not specify and although had foresight to connect it I did not have the foresight to check it. The cable is well buried and upgrading is not an option . So we are where we are. I have buried 12m x 2.5 mm. Armoured cable 3 feet deep across garden with electrical hazard tape above. Fitted a 4 foot earthing rod and am planning on fitting 2x surface mounted double sockets with conduit+ ferules + and a couple of LED strip lights all attached to a mini garage consumer unit which comes pre loaded with 63a , 30ma RCD + 16a +6a mcbs . So 2.5mm radial circuit = 16a max load but typically consumer unit has 2 separate breakers 1 for lights and 1sockets. So my question is as I have limited amps and want to maximise sockets is it ok to just have the one MCB at 16a and run both lights and sockets from it or would this be frowned upon? Alternatively is it ok to plug led strip lights into sockets and just use sockets as switches . Or lastly is there another combination of mcbs or an alternative solution to maximise my consumer unit. For reference usage in garage will be worse case scenario 1x small pillar drill or pressure washer or bench grinder at a time + freezer + led lights . Heat is supplied by oil burner. Any help would be greatly appreciated.
 
I'm intrigued to know why you want to feed the lights from a 16A MCB when your CU has a 6A one fitted?
So in my unedumacated little brain , if the 16a breaker is fully loaded and a partial short occurs on the 6a breaker the current draw on the combined could exceed the 16a rating on the cable ? But suppose I'm covered by the breaker on the main board ?
 
You don't need either the consumer unit or the earth rod (unless you've got metal service pipework entering the shed from underground).

If the feed from the house CU has RCD protection then you will not need RCD protection at the shed, if not then you will need RCD protection but this can be a standalone device in an enclosure.

You can just wire it as a radial circuit and use a switched fused spur or a fused spur to feed the lighting.

You may be able to change the 16A MCB for a 20A MCB but this will be subject to confirmation of the earth fault loop impedance at the shed.

Installing a consumer unit in the shed will be pointless as the MCBs in it will.not discriminate with the 16A MCB feeding it and faults will cause both to trip.
 

Reply to Consumer unit MCB selection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
1K
  • Question
Why would you want to fuse them? The RCD should now be a type A plus it is likely you could upgrade the protective device to 20A. What protective...
Replies
3
Views
1K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
Replies
15
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks