FatAlan

-
Trainee
Nearly Esteemed
Supporter
Joined
Sep 16, 2016
Messages
2,065
Reaction score
1,993
Location
Surrey
Ok, so you have a motley collection of old BS3036 fuse boxes that need to be replaced by a new consumer unit. Existing installation tests all good but the T&E coming out of the wall is spread out and not long enough. What do folks do to extend cables or what’s the recognised best practice to ensure a neat and compliant job? Any pics?
 
Obsolete VOLED and no RCD. Was on a TT with very high Ze. Couldn’t locate the earth rod and suspect it’s burried under old extension. DNO has now put in a PME connection and Zs now good.
[ElectriciansForums.net] Consumer Unit replacement cables not long enough.
 
Reckon the top box will be ok but the three circuits from below could be extended. Just looking for views on seperate enclosure, and connections really. Extending initial legs not option as classic case of client having loads of work and decorating done without thinking about the electrics until too late :rolleyes:
 
For only four cables needing to be extended upward I would just put a junction box on the wall at the point of the lower consumer unit and push fit wire connector the cables upward to a new CU at the MEM board position. It hardly justifies the use of a DIN rail enclosure, though it would be neat.
 

Reply to Consumer Unit replacement cables not long enough. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K
  • Question
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about...
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top