Ross Trician
Hello all,
I went to look at a job today that I have been asked to price for but I am abit confused at the way the c.u is fed.
The job is a bowling green club house thats being extended, the cu tho is fed from the meter of the tennis courts, about 40m away.
it is run in 2 core swa that look to be maybe 16mm max. they have used the armourings as the cpc.
the main cutout is 100A,
would I be right in saying the supply cable needs to be suitably rated to match the cut out fuse?
also is it allowed, (whether morally or not) to use the armourings as the cpc to supply the c.u?
been looking in the big red book but cant seem to see the obvious if its there..
I am thinking it wants the cable changing to 3 core and25mm, Subject to the volts/amps drop etc for the distance.
thanks, Ross.