Have to quote on a consumer unit replacement, problem is gas meter is next to existing consumer unit 25 mm between them, they are both in a wooden cupboard,
What would you do
 
Tricky one. Gas regs need 150 mm I think. Might be worth having a good read of the gas regs and seeing if a barrier of some description solves the problem.
Otherwise its an IP box, din rail, din terminal blocks and move the CU.
Or convince them to move the gas meter!
 
Maybe this will help:

BS6891-2005

8.16.2 Separation of installation pipework from other services

Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows:

a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
 
My reading of that is that if suitable “electrical insulating material” can be arranged there is no distance limit. I wonder what constitutes such a material. Presumably more than empty pvc trunking.

The only time I’ve had this issue it was not the only problem, trying to find a CU that fitted the space was hard with or without the gas pipe. I’m wondering if that applies to this situation too, e.g. if a rewireable wylex only just fits then fitting anything new in was next to impossible anyway.
 
Might be easier to insulate the gas piping. There are pvc sheaths that fit around 15mm & 22mm pipe; used cosmetically for radiator pipe drops. For main gas incoming idk maybe wrap some tape around it. Sometimes main gas piping is sleeved with yellow plastic; I guess this negates yhe 15mm away electricals rule !
 
Might be easier to insulate the gas piping. There are pvc sheaths that fit around 15mm & 22mm pipe; used cosmetically for radiator pipe drops. For main gas incoming idk maybe wrap some tape around it. Sometimes main gas piping is sleeved with yellow plastic; I guess this negates yhe 15mm away electricals rule !

Cant' imagine the decorative pipe sleeving will count as suitable insulating material far as the regs go!
 
Cant' imagine the decorative pipe sleeving will count as suitable insulating material far as the regs go!
The pipe sleeving is made of PVC, which is an 'electrical insulating material', so why not?
I'd consider dry plywood to be an 'electric insulating material' as well, so I'd be happy with a piece of 6mm plywood dividing the cupboard.
 
The pipe sleeving is made of PVC, which is an 'electrical insulating material', so why not?
I'd consider dry plywood to be an 'electric insulating material' as well, so I'd be happy with a piece of 6mm plywood dividing the cupboard.

The clip on pipe trim is made of material of an unspecified nature as far as electrical insulation goes. It's only purpose is to make copper rad pipes look acceptable. Must be barely a quarter of a mill thick also.
 
Here's my cu with the gas pipes adjacent, the white pipes are clip around sleeves and the yellow is the gas incomer, the yellow insulation is insitu and part of the pipe when it was installed. I used the CU for Stroma assessment years ago and had no complaints at the time ! And it's not blown up, yet 😀 The DNO replaced the head at the time and no qualms from them either.

[ElectriciansForums.net] Consumer unit too close to gas meter
 
Last edited:
Here's my cu with the gas pipes adjacent, the white pipes are clip around sleeves and the yellow is the gas incomer, the yellow insulation is insitu and part of the pipe when it was installed. I used the CU for Stroma assessment years ago and had no complaints at the time ! And it's not blown up, yet 😀 The DNO replaced the head at the time and no qualms from them either.

View attachment 93103
QED, I think.
 
I had this the other day. Needed to replace the old fusebox right next to the incoming gas pipe. Looks like they had a smart gas meter fitted fairly recently and whoever did it has covered the gas pipe with some sort of clear PVC sheath.

I'm assuming this is them covering the pipe with an electrically insulating material to comply with regs?
 

Reply to Consumer unit too close to gas meter in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
315
  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top