Appreciate a bit of advice regarding this that I'm doing in the morning-
Consumer unit upgrade in house with 6mm gas & water bonding existing (leaving bonding as it is). Existing rod in house with 6mm up to CU.
(Existing install) From a TT system in the house there is a 2.5/1.0 T&E running to a detached outhouse (perhaps, four meters from the back of the house) feeding an existing fuseboard in there with BS3036 fuses for 15A sockets radial and 5A one light.
The outhouse has a copper water pipe supplying a washing machine. This isn't bonded where it rises from the concrete floor in the outbuilding and there isn't a seperate rod in there. The only earthing of anything in there is the 1.0mm CPC of the T&E submain & CPCs of light/sockets.
Am I right in thinking that the CPC in the T&E won't suffice in the requirements for equipotential bonding in the outbuilding (it appears that the T&E is ran under the concrete back yard in plastic conduit.. many years ago). If I install a rod & earth conductor to the existing BS3036 unit in the outbuilding and bonding between this unit & the copper pipework in the outbuilding, should I insulate the 1.0mm CPC in the T&E submain from the outbuilding installation (at the outbuilding end)? Or leave it connected at both ends- in the house and the outbuilding. If either is acceptable would it be best practice to leave it connected both ends?
I am quite aware of requirements when exporting TNS and TNCS but I've never came across TT in the main building with an outbuilding where bonding is required.
This is hopefully obvious to one of you who may read this before tomorrow
Consumer unit upgrade in house with 6mm gas & water bonding existing (leaving bonding as it is). Existing rod in house with 6mm up to CU.
(Existing install) From a TT system in the house there is a 2.5/1.0 T&E running to a detached outhouse (perhaps, four meters from the back of the house) feeding an existing fuseboard in there with BS3036 fuses for 15A sockets radial and 5A one light.
The outhouse has a copper water pipe supplying a washing machine. This isn't bonded where it rises from the concrete floor in the outbuilding and there isn't a seperate rod in there. The only earthing of anything in there is the 1.0mm CPC of the T&E submain & CPCs of light/sockets.
Am I right in thinking that the CPC in the T&E won't suffice in the requirements for equipotential bonding in the outbuilding (it appears that the T&E is ran under the concrete back yard in plastic conduit.. many years ago). If I install a rod & earth conductor to the existing BS3036 unit in the outbuilding and bonding between this unit & the copper pipework in the outbuilding, should I insulate the 1.0mm CPC in the T&E submain from the outbuilding installation (at the outbuilding end)? Or leave it connected at both ends- in the house and the outbuilding. If either is acceptable would it be best practice to leave it connected both ends?
I am quite aware of requirements when exporting TNS and TNCS but I've never came across TT in the main building with an outbuilding where bonding is required.
This is hopefully obvious to one of you who may read this before tomorrow