I have been going over this for some time, and every time I think I have it sorted I read something else which sows doubt in my mind again!

TT system.

CU to be replaced and moved to new location as not enough room where currently sited.

New location will result in tails being approx 5m in length and running short distance under floorboards.

Current set up would be DNO Fuse > Meter > DP Isolator > CU with 100mA TD RCD and 2 x 30mA RCD.

To reach new location I had planned DNO Fuse > Meter > DP Isolator > Switch Fuse > 25mm SWA > CU with 100mA TD RCD and 2 x 30mA RCD.

Do I need up front RCD protection of these "extended tails"?

I have read 522.6.204 (iv) to mean it is not required.

Would appreciate thoughts of those wiser than myself to stop me going round in circles.

Timotei
 
I would fit a 100mA DP rcd with adjoining overload protection next to the cutout.
I would then wire DB supply using a method like SWA etc to ensure the need to cover at 30mA is not required and then supply a standard main switched board with 30mA cover where required.

Result is, all sides of your butt is covered :) regarding the regs and installation safety.
 
Thanks, bit of a "can't see the wood for the trees" - upfront RCD it is then!

Didn't seem right without it, but kept coming back to that reg and then running round in ever decreasing circles!

Appreciate your help.

Timotei
 

Reply to Consumer's Tails > 3 metres - RCD or not RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
398
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
696
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top