Contactor for lighting | on ElectriciansForums
Discuss Contactor for lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
lancashire
hello everyone i havent posted for a while but i know this is the place for my answer, if i was to put a contactor in for a lighting circuit how is it wired/connected also if would any contactor have any effect on rcd's within the circuit?
cheers malcolm the reason i was asking is a rewire may be coming up were the cust wants to be able to switch up and down lights off on her way out of the house via a switch and as its quite a big house so i was thinking of doing it via a contactor in the db, the 2 way switch and down landing light are to be wired separatley from this arrangment. any thoughts??
20 amp double pole key switch - Solves the kids problem if there is one. Couple of keys for keyrings and away you go. Maybe a little overkill for a domestic but it would do the job - easy to wire (Especially if you are unsure about contactors - although they are Not hard once you have done 1 you can do them all imho.).
unusual for domestic i'd say but i'd go the contactor route
1 pole per circuit at the db-bit more flexiblity in case additions ever needed
de-rating of ac-1 contacts is needed for tungsten or fluorescent
ya ac-1 is resistive load- immersion etc
i think you may need to de-rate the modular contactor for incandescent lighting if that's what you're switching
ac5b is incandescent -i think you'd de-rate a 20amp modular to ten for standard bulbs if i'm not mistaken
Reply to Contactor for lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...