Hi looking for some advice, looking to put some outside heaters (in my garden) 2 x 2500w, now I want a time delay switch but this can only switch 16A, so I’m looking at putting a contactor in as I already have one, but I’ve only ever used contactors twice before, is this the best way to set up and is drawing fine?
Thanks
 

Attachments

  • [ElectriciansForums.net] Contactor for outside heaters
    E03FBDB9-E761-4B84-9E63-E5D7F7244351.jpeg
    78 KB · Views: 49
It does make a difference, and it doesn't have to be a fuse, a 1A MCB is fine.
Why does it matter? Aslong as the control circuit isn’t higher than the supply circuit?
It doesn't really make any difference, nor does it matter. Either use a 6a mcb or a 1a fuse/mcb, either way the control part of the circuit is protected. The only reason you might decide on a lower rated device over a 6a mcb is to ensure only the local device operates in the event of a fault on the control circuit. However as nothing will operate if the control circuit fails it hardly matters if both devices operate.
 
Hahahaha oh well
Where is Greta when you need Her?
[automerge]1581273452[/automerge]
Why does it matter? Aslong as the control circuit isn’t higher than the supply circuit?
But you can install the fuse in the same enclosure as the contactor rather than takev up any spare ways in the CU for a 1Amp cb.
 
Depends on the size of the enclosure Dave, doesn't it, a "slideloc" fuse is the best option I reckon.

The size of the enclosure should be chosen to suit what is being installed, not the equipment chosen to suit the enclosure.

You might have to fire up the old time machine to get a slideloc these days, I haven't seen one of them new for years.
 

Reply to Contactor for outside heaters in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
304
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top