If it's a commercial mixer there will almost certainly be a safety interlock on the head, if it hinges or on the bowl guard if there is one.
The interlock will be in the control circuit for the contactor.
What you shouldn't be able to do is get your hands / fingers anywhere near any moving parts when it's running.
Indeed. there could be more than one safety interlock - example bowl height and then blender guard.

More information needed. When you don't know the answer - gather more data

Edit: just seen the post where the original poster mentions the difference is this machine has a stop / start.
Excuse this question to original poster, because I do not know anyone here, how familiar are you with DOL starters and auxillary contacts?
 
Late to the party on this one as well, but if the original contactor had a NC auxiliary contact and the circuit is single phase, then one of the main contacts has been used as the aux to hold the contactor on, and as already said, the fault will probably be with a safety circuit external to the contactor.
I'd be getting a pen and some paper and tracing out the circuit of a) what I have with the faulty machine, and b) what it should be, from the adjacent, working, and hopefully, unmolested machine, if it is identical.
 

Reply to Contactor not latching in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Commonly known as double knock, some pirs have a latch on time delay for a few seconds, giving time for the 2nd one to activate .
Replies
3
Views
354
Hi, I need to rewire a mapping/traction control switch on a race bike that was damaged in a crash. The switch is not stock to install some other...
Replies
0
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top