hi wiring up this single phase contactor for lights which are wired in 3 core, I presume they just terminate Brown 2T1 and Blue 6T3 cheers never has experience with a contactor before and earth to earth bar
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Contactor wiring on outdoor lighting in the UK Electrical Forum area at ElectriciansForums.net
thats no use, i will have a wordNo Mate Shirley forgot to put it in the box with the contactor
Agreeand if no bit of paper, crack out the continuity tester and figure it out
Agreeand if no bit of paper, crack out the continuity tester and figure it out
And I'm president ObamaPete - he is a "spark"
I Knew It !!!!! It's the eyes in your photo that gave it awayAnd I'm president Obama
im bashar al assadAnd I'm president Obama
im bashar al assad
Mmmmm! Trump with electrical knowledge?...Thank god your not trump
HeOP: Yes.
The terminal numbers indicate the contact functions. L1, L2, L3 are the line side and T1, T2, T3 are the load side of the 3-pole main load circuit contacts, as per NEMA coding. 1,3,5 and 2,4,6 are the equivalents using the IEC coding scheme.
So provided the circuit going in on L1 & L3 is the lighting supply and has the necessary protection upstream of the contactor, then the luminaires connect to T1 & T3.
Wasgoing to say something along those lines but chickened out.And I'm president Obama