Contactor wiring ?

Can I ask why the neutral is switched as well? Most of the contactors I see are just switching the supplys

when 1 of the mats goes down with a N-E fault, the RCD will be glad of the 2 pole isolation.
 
I've laid a couple of those mats under tile before but never connected up to the room stat, are they not usually two wire elements anyway? Not being arsey just trying to learn new stuff!
 