J

jon090

Hi, im installing a timeclock with contactor for a lighting circiut in house.

Do i need a seperate feed from a seperate breaker for the contactor in addition to the lights feed on B6 breaker, or am i able to loop the two (from the coil side, to the incoming side of the contactor) protected from the same B6 breaker? The total load is aprox 2Amps.

Any advice would be helpfull - Cheers
 
Both methods are acceptable.

If the contactor is only controlling 1 circuit then loop it from the coil, if the contactor is controlling more than 1 circuit give it its own breaker as this will make testing easier

Tim
 
What would sort of inductive loads could you expect to see in a lighting circuit and where would they come from? I am only familiar with inductive loads generated by maybe an electric motor or transformer and so on. Educate me
 
I've had a couple of jobs where we provided HID perimeter lighting one on a time switch with light sensors and one using remote wireless controls. In both cases the control circuit was on its own separate 6A MCB and the contactor fed a dist. Board.
I always include a manual override switch.
 
I just did a load of reading up on it. Typically incandescent are resistive yes, but you can still get magnetic inductive incandescent lamps.

Not a particularly exciting lunch time i must confess.
 
It's discharge lighting thats inductive, I'm guessing a son or HQI type in this case. It's down to the ballast.

Incandescent isnt, thats a resistive load.

Agree, along with old ballast type florries.
I was simply intrigued that the timeswitch wasn't rated for 2A. Most will handle at least that, even as an inductive load.
 

Reply to contactor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
687
davesparks
D
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top