Hi people, new to this forum.

just went to do an EICR and the upstairs lights aren’t RCD protected. Rather than fail it and say it needs a board change, I’d like to the circuit on an RCBO.
The Consumer Unit is an older style Emma/Contactum board. Am I right in thinking a new miniature Wylex RCBO will fit in there? There is a circuit on a Wylex MCB, so that’s why I’m thinking it will fit.
Just wanted some advice before I go and source the RCBO.
Thanks in advance
 
Why would it 'fail' and EICR? I would only code that a C3 which would still attract a satisfactory report. If a special location is fed from part of the circuit then I would look at the existing lighting within the location and check that supplementary bonding is in place, if all is good then no C2.
 
The Wylex device should not be there so needs Coding. Contactum produce compact rcbos.
Agree, westy...but if the RCBO won't fit in the older CU, would you reckon it's still a C3 for no circuit rcd......... and the Wylex cb still in place? ?

Do two C3's add up to a C2??...or a C6??
 
Hi people, new to this forum.

just went to do an EICR and the upstairs lights aren’t RCD protected. Rather than fail it and say it needs a board change, I’d like to the circuit on an RCBO.
The Consumer Unit is an older style Emma/Contactum board. Am I right in thinking a new miniature Wylex RCBO will fit in there? There is a circuit on a Wylex MCB, so that’s why I’m thinking it will fit.
Just wanted some advice before I go and source the RCBO.
Thanks in advance
Hello. Alan here from contactum technical support. Could you please let me have a part number from one of the Contactum MCBs within this board. Ill then be able to assist you further. please email me at [email protected]. Kind Regards Alan Broom TMIET
 

Reply to Contactum CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
709
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top