On my cu at home I have a continuity reading between my ring final circuit and a radial circuit of 114ohms between live conductors.

When I test continuity from each breaker.

Why would that be? Break down of cable

If I turn one off and leave the other on I don't get a voltage.

At what point would a voltage appear between them or would it trip the rcd?

I'm to lazy to unplug every thing and do an Insulation resistance test between the 2 cirxuits
 
If you are testing for electrical separation, you must disconnect the neutrals of the circuit under test as well as isolating the line conductors. It's entirely possible you are reading the apparent resistance of a circuit that goes something like this....

line conductor on ring -> some load -> neutral conductor on ring -> neutral bar in consumer unit -> neutral of radial circuit -> some load -> line conductor on radial circuit
 
If you are testing for electrical separation, you must disconnect the neutrals of the circuit under test as well as isolating the line conductors. It's entirely possible you are reading the apparent resistance of a circuit that goes something like this....

line conductor on ring -> some load -> neutral conductor on ring -> neutral bar in consumer unit -> neutral of radial circuit -> some load -> line conductor on radial circuit
Ah that makes sense. ?

I will try that in the morning.

so with Insulation Resistance Though you can test off the neutral bar and or earth bar and the breakers though right?
 
Yes, but if you use the neutral bar you will test the neutral of all circuits at once, and the line of any circuits that have load connected (you should not apply insulation tests between line and neutral of loads). To test circuits individually you must disconnect their neutrals from the bar.

Agree with @SparkyChick that 114 ohms is probably the resistance of loads on the two circuits in series. It is not impossible, but very unlikely, for any cable fault to read in the hundreds of ohms. Copper touching copper is likely to be an ohm or less, while even burnt or wet insulation is likely to be tens or hundreds of kilohms.
 
Yes, but if you use the neutral bar you will test the neutral of all circuits at once, and the line of any circuits that have load connected (you should not apply insulation tests between line and neutral of loads). To test circuits individually you must disconnect their neutrals from the bar.

Agree with @SparkyChick that 114 ohms is probably the resistance of loads on the two circuits in series. It is not impossible, but very unlikely, for any cable fault to read in the hundreds of ohms. Copper touching copper is likely to be an ohm or less, while even burnt or wet insulation is likely to be tens or hundreds of kilohms.
Thanks for the replies :)

I was just curious as all....before I brought the property the neutral in the main switch had burnt out.

And the board was replaced, what would cause that? Would the neutral cable have just become loose over the past 40 or 50 years or could the problem have been else where

It was an old wylex cartridge barkelite fuse board
 

Reply to Continuity between live conductors in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top