Hello I was wondering if anyone could help me on what is the most appropriate method to test continuity of cpc on a 2 core steel wire armoured cable to a distribution board.
 
Welcome to the forum ajay123 :)

I've relocated your thread to the correct section, if you are currently on a active training course you may benefit from our trainee section, just apply providing all the required info requested.
 
Not sure how that would help you verify cpc continuity unless I'm misunderstanding you.

method 2 may not be a viable option due to distance etc.

In order to get a value for the armour being used as the cpc you would need a value for R1 first to subtract from the reading of the R1+R2.

Am i missing something?
 
I would say that you may need to check that the armour gland is not still connected to other metalwork that may provide an alternative path for your measurement.
Other than that as simonslimline says measuring R1+R2 will record continuity of the armour, and subtracting half the R1+Rn value would give you a resistance value for the cpc.
On average the resistance of the armour would generally be about 1-1.5 times the R1 resistance for 1.5mm² cable and drop down to about 1/3 of the R1 resistance for 25mm² cable.
 
But how would I connect line and the steel wire together at one end of the cable, and then after I can just put one test probe on the gland on the other end of the cable and the other probe on line
 
But how would I connect line and the steel wire together at one end of the cable, and then after I can just put one test probe on the gland on the other end of the cable and the other probe on line


Are you familiar with the methods i mentioned?

Method 1 and method 2.

Invest in a copy of guidance note 3, it would be beneficial to you mate.
 
Last edited:
In order to get a value for the armour being used as the cpc you would need a value for R1 first to subtract from the reading of the R1+R2.

Fair enough, but we're not actually interested in the phase conductor resistance but simply that we have adequate continuity on the cpc. But I realise that knowing what resistance the cpc should be for the length expected is important.
 
Fair enough, but we're not actually interested in the phase conductor resistance but simply that we have adequate continuity on the cpc. But I realise that knowing what resistance the cpc should be for the length expected is important.


Using method 2 long lead test would be a simpler way of achieving this in all fairness. However if the SWA is a long distance then this method might not be viable, hence using method 1 Between Line & Neutral to get a value to subtract from the method 2 result between Line and CPC/armour.
 

Reply to Continuity of cpc on 2 core SWA cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
274
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top