A
ajay123
Hello I was wondering if anyone could help me on what is the most appropriate method to test continuity of cpc on a 2 core steel wire armoured cable to a distribution board.
Discuss Continuity of cpc on 2 core SWA cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Maybe worth noting that the op is a trainee according to the profile.
Method 1 or method 2 depending on distance i guess.
If method 1 then do it between line and neutral first and half the reading to get a value for R1.
Not sure how that would help you verify cpc continuity unless I'm misunderstanding you.
But how would I connect line and the steel wire together at one end of the cable, and then after I can just put one test probe on the gland on the other end of the cable and the other probe on line
In order to get a value for the armour being used as the cpc you would need a value for R1 first to subtract from the reading of the R1+R2.
Fair enough, but we're not actually interested in the phase conductor resistance but simply that we have adequate continuity on the cpc. But I realise that knowing what resistance the cpc should be for the length expected is important.
Reply to Continuity of cpc on 2 core SWA cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net