thats exactly how ive always seen it whensbait. i reckon thats another cock up in gn3 but it would certainly be the way to go in my predicament.
OK consider this example I have just made up.
I have a circuit 50 metres long.
resistance of copper at 20 degrees(all approximate to illustrate example)
1.5mmsq =12 milliohms/metre
1.0mmsq =18 milliohms/metre
so 1.5/1.0 t+e =30 milliohms/metre
Now if I measure at ceiling rose (line side,forgetting about switch drops for a moment) R1+R2=50x30=1500 mohm or 1.5ohms
So,say we have a distance to switch of 10m
we would now have to add the switch wire lengths to get reading at ceiling rose.:12x20=240mohm +1500=1740 or 1.74ohms
Now if I measure at the switch( only one leg of twin)
we would have to add( 12x10=120 )+(18x10=180)=300mohm+1500=1800
or 1.8ohms. So it looks like the switch in this example wins.
Of course if we are using loop tester we should bear in mind Jasons advice that we may need a circuit neutral when testing thru rcds.