continuity of final ring circuit conductors | on ElectriciansForums

Discuss continuity of final ring circuit conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Jan 7, 2011
Messages
50
Reaction score
5
Hello,

I am about to conduct my first initial verification and i have spent all weekend reviewing how to do the recommended tests. However I have a question regarding final ring circuit test.

1- is this only for a ring main circuit with outgoing line and incoming line?
2- if the answer is "yes" what happens if the ciruit is a spur from the distribution board?

cheers

DD368
 
first, you measure the end to end on the RFC, r1,r2,rN. you would expect r1 and rN to be identical, and r2 to be 1.67 x r1 ( 2.5mm L/N, 1.5mm cpc.) then you x connect L and E at the CU and measure R1+R2. ( expect this to be (r1+r2)/4. this reading should be the same at every socket, except if you've got a spur, where the reading will be higher.
 
You will only do a ring final continuity tests on a ring final so that will be your tests for that.

If a spur is taken from the CU off of that RF then you will connect that the spur cable to say LINE 1 CPC 2 when you do the R1+R2 results and then take your reading around the ring as normal. If you so wish you could also again connect up when you do the LINE 2 CPC 1 side but thats being overly enthusiastic. After doing both sides you obviously note the highest value on your certificates.
 
does anyone do step 2?
After end to end resistance on L N CPC, cross connecting one outgoing line conductor to the returning neutral conductor and vice versa expected results (r1+rn)/4 and then doing step 3 cross connecting outgoing line returning cpc and vice versa expected results (r1+r2)/4.
 
mate you have to do step 2 and 3 or you hvant completd the test correctly just carrying out end to end and using the calculated as your reading isnt correct and if there are spurs wont be accurate the
r1+rN/4 gives you the calculated for comparison with the measured at step 2 and then repeat for step 3 and record the highest line to cpc as your measured R1 +R2
 
YES you MUST do both, If you don't you would not find a live earth reverse!!

I agree that you are required to conduct the test for a ring final circuit, but the dead polarity test, R1 + R2, won't detect a line/cpc reversal either. Inspection is more important than testing.
 
Isn't that why you do an R1+Rn as well on a ring final?

Like I said it is required for testing continuity of ring final circuit conductors. The point I am making is that it is not a standard test for radial circuits so inspection is also important for polarity.

Tests are very much SECONDARY to inspection.
 

Reply to continuity of final ring circuit conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top