Hi

Just doing end to end test

line - line 0.51ohms seems fine

cpc-cpc 0.91 ohms seems fine

But N- N reading is coming up 1.46 Kilo ohms ??!!! any thoughts

I am doing 2392-10 and am fairly green.............be gentle

angus
 
Definitely as above.

I have had similar, and all it took was a half turn with the screwdriver to go from about 500 ohm to about 0.45ohm.
Fortunately, it is just this easy sometimes.

Cheers........Howard
 
yeah definatley a bad connection had a line-line the other week when checking for a kitchen fitter, 4.46ish k ohms. Turned out to be a poor connection and burnt out in the back of a socket.
 
it's finding where to use the screwdriver that's the hard part

Depends where you're testing.
I&Ting hotel bedrooms once, virtually every room the RFCs had bad readings and just about every socket we removed to look at had loose connections or just pulled out completly. The manager was not happy, only rewired a few years earlier. We left him digging out the installers details.
 
Not always a bad connection, had it before where the installer had twisted the conductors together and it had broken, giving a high end to end reading. More often than not it will just be a dodgy connection.

Just gotta hope it's at a socket and not a JB under the floor!

Is this a question in theory or something you have just come across in the field?
 

Reply to continuity of ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top