rosscohans

Hi. be nice for some feed back on this. I'm testing a ring main for an eicr. I know that the cpc reading should be around the 1.6 times higher than the live conductors but I'm getting 0.66 on live, 0.67 on neutral and 0.61 on cpc. I'm wondering, if the cpc are connected through the metal k.o box on some points would this bring the reading down? As I've checked every socket and all seems fine.
 
Is it in twin and earth or singles? If singles then the cpc is more than likely the same CSA as the live conductors and consequently the same resistance, within a range of about 0.05 ohms.
Additionally the cpc of an existing installation can have parallel earth paths and so can produce much lower readings.
carry on with the other crossover tests to confirm its a ring etc
 
On te 2.5mm the earth is 1.732 greater resistance . As mentioned above, parallels?

Actually on a 2.5mm twin cable the cpc is 1.5mm which is 1.67 x smaller which produces a resistance which is 1.67 x higher than the line conductor. This is the norm.
A parallel path is a secondary route to earth other than the primary cpc path. Examples are main bonding conductors, supplementary bonding etc etc
These paths will reduce the resistance and consequently your resistance readings may be less than you would expect
 
Last edited:
As has been said above the CPC in this circuit is the same size as the Line and neutral weather its 1.5mm, 2.5mm, etc
Even if the CPC did go though back boxes it would not make any difference - however if you had metal trunking/conduit and that was used as the CPC that would bring the r2 down.
 

Reply to continuity on ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
761
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top