continuity test on rfc | on ElectriciansForums
Discuss continuity test on rfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
stv292
hi all
i'm doing a continuity test on rfc
r1=.70
rn=.69
r2=1.14
but when doing r1+rn/4 it should be .36 but getting .74 on all sockets
and r1+r2/4 should be .46 but getting .83 on sockets
is this just due to loose connections somewhere
thanks in advance
are you cross connecting the L and E at the CU to measure your R1+R2, with the cables disconnected from their respective CU terminals?
Have you tried taking the sockets off and measured at the terminals.
Had the same problem a few months ago and it was down to cheap arse sockets!!
Reply to continuity test on rfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
I believe that it is incorporated into the 5 days. But will double check. Thanks.