Cables in con unit suggest bonding to gas and water.but I can't find connection..is there a way i can I test for it
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.
 
Overskilled that is what Richard pointed out even doing a R2 test there is a good chance that you will get some sort of reading if there is metal work throughout the installation, by picking up parallel paths.

If you don't get a reading of any kind then I would do an IR test with the MET to confirm that there is no potential
 
Overskilled that is what Richard pointed out even doing a R2 test there is a good chance that you will get some sort of reading if there is metal work throughout the installation, by picking up parallel paths.

If you don't get a reading of any kind then I would do an IR test with the MET to confirm that there is no potential
Wasn't a reply when I hit post. Consider entry retracted
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.
Agree with this 100%
 
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.

Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?
 
Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?

That figure is suggested for the resistance of the connection to the part being bonded only, not the bonding cable. Ie you test between the cable terminal of the earthing clamp and the pipe it is attached to and this should have minimal resistance with 0.05 being the suggested guideline maximum
 
That figure is suggested for the resistance of the connection to the part being bonded only, not the bonding cable. Ie you test between the cable terminal of the earthing clamp and the pipe it is attached to and this should have minimal resistance with 0.05 being the suggested guideline maximum

Are you sure about that? I think the ruling is that the recommendation is that the main bonding' resistance should be 0.05 Ohms, anything greater then you should look into increasing the CSA of your main bonding conductor. The figure of 23Mohm relates to the resistance of any extraneous metal work measured from a known earth, anything less then that makes it an extraneous part and thus should be bonded.
 
Last edited:

Reply to continuity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
729
loz2754
L
I also connect the 2 bars to the side bolt on these, the coarse, rounded thread screws hager use can work loose. All those bushes and glands sat...
Replies
4
Views
388

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top