GN3 only suggests that the resistance of a main bonding conductor should be in the order of 0.05Ω, however this is patently incorrect as I have measured bonding conductors reading 0.00Ω on my meter!Would you ever use the 0.05Ω suggestion Richard in GN3 to confirm a bonding connection if the bonding clamps are unable to be found?
Not with surety.
All you can say is that the connections are not available for testing (however they should be available for testing, but are often boxed in)
Even if you test continuity from the MET to the nearest point of entry of the metallic service you will very likely get a low reading as there will be interconnections from boilers, etc that will give a low reading so it cannot be proved there is bonding present without being able to test the end to end continuity of the bonding cable.
However if you test continuity and you get a high reading then you can almost certainly say there is no bonding or it not connected.
Whats wrong with powering down and disconnecting the bonding conductors from the MET, then measuring to the gas / water pipe where accessible?
True....Will still give a much better clue than just connecting to the MET